The breaker popped a second time. I left it off.

 

If I go get the RMTEX-06, it's 240V. I'm already wired correctly.

 

If I throttle it down with a mixing valves will it use a little less electricity, but not trip the breaker?  ...it shouldn't...

 

Link to comment
Share on other sites

Anytime it's heating, it will draw the same amount of current. 10ga wire minimum. 

 

Your guide shows a 1P 30a breaker for the 220v 06 model. You don't have 220v on a 1-Pole breaker.

The guide is a little misleading. Europe. You can;t get 220v on one phase using the neutral at your house.

You would have to wire 1 Line directly hot instead of the neutral. Don't do it.

Baseboard heaters were allowed to do that in the sixties.

NEC put a stop to that bullshit.

 

Neither the 04 and 06 have a thermostat. You need to rethink this application.

If you have 10ga wire in the wall, connect one Line to a 30A 1P breaker, one line to neutral for 120v.

Since you don't have temp control, you can do the mixing valve thing or buy one with a thermostat.

Bill, don't run it anymore until this is corrected.

 

The 220V 1ph is Europe. That can be confusing.

In the U.S., and in fact everywhere in North America, the standard voltage is 110 V (with a frequency of 60 Hz) rather than the 220 volts used in Europe. The 06 model will not help your situation.
Edited by CALCXX
Link to comment
Share on other sites

  • 2 weeks later...

Bill, the guide is misleading. Remember, your name plate says 120v. 

You don't have 220v on 1 phase. Nameplate is everything.

Ask your home insurance agent what he thinks about supplying 220v to this 120v rated appliance.

Edited by CALCXX
Link to comment
Share on other sites

  • 2 weeks later...

Bill, we use under-sink water heaters in all of our clean rooms, and I have had to fiddle with a few. 
I am not sure what V they are on and I am off for the week, so won’t know till next week. 
That being said, I do know that in our units the temp rise or fall is controlled by water flow, not thermostat (which is non-existent AFAIK) Increasing the flow lowers the temp, duh.

Hope this helps.

Link to comment
Share on other sites

100% of water heaters have thermostat.  But like the conversation about EV parts and "what is a tachomoter," how it's employed and the results you see may vary.  There is absolute no heating appliance sold in the US that doesn't have an over-temp thermostat.  Now, what other benefits are written into the software controlling it (and yes, pretty much everything has some form of crude software), will vary.  And as you noted, even just an "on" command could still mean you run past the heating ability.  I would expect better quality units would use good software PIDs and a high-watt heater to hold a fixed temp no matter what.  Would be easy really.  PID software is commonly used for everything that needs to have predictive control, from quadcopters to advanced cruise control to...heating...

 

 

Link to comment
Share on other sites

Also the above post is totally useless for Bill's needs and I just love exploring the hidden world that runs our lives.  Without a PID, my toaster oven could not make perfect toast, as it does.

 

Link to comment
Share on other sites

4 hours ago, RXX said:

Bill, we use under-sink water heaters in all of our clean rooms, and I have had to fiddle with a few. 
I am not sure what V they are on and I am off for the week, so won’t know till next week. 
That being said, I do know that in our units the temp rise or fall is controlled by water flow, not thermostat (which is non-existent AFAIK) Increasing the flow lowers the temp, duh.

Hope this helps.

Your thermostat may be only a set-point. When it gets hot enough, it shuts off. That's what mine does. If the gas water heater eventually sends water hotter than the POU heater thermostat (sensor) requires, it just takes a break.

 

Link to comment
Share on other sites

2 hours ago, SwampNut said:

100% of water heaters have thermostat.  But like the conversation about EV parts and "what is a tachomoter," how it's employed and the results you see may vary.  There is absolute no heating appliance sold in the US that doesn't have an over-temp thermostat.  Now, what other benefits are written into the software controlling it (and yes, pretty much everything has some form of crude software), will vary.  And as you noted, even just an "on" command could still mean you run past the heating ability.  I would expect better quality units would use good software PIDs and a high-watt heater to hold a fixed temp no matter what.  Would be easy really.  PID software is commonly used for everything that needs to have predictive control, from quadcopters to advanced cruise control to...heating...

 

 


“There are no facts…… just interpretations”

-Nietzsche

 

FlowCo™ is a reliable non-thermostatic water heater delivering endless hot water on demand. FlowCo™ is ideal for single, sensor faucet or single, metering faucet for handwashing and other fixed-flow applications. The heater features self-diagnostics with intelligent controls, SafeStart™ technology, and 3/8" compression fittings. InfoCue™, a visible LED indicator, indicates system status and operation feedback. The unit mounts in any orientation and is compact in size.

Link to comment
Share on other sites

It's like that tachometer.  The Zero has one, the Tesla doesn't.  No wait, of course, it has one, like every heating device has a thermostat.  But we just don't show it, or use it in a way that you can tell.  But we have to know, so we don't blow up.  But you get no benefit other than not blowing up.

 

 

59597.jpeg

 

41815.png

Link to comment
Share on other sites

It isn't adjustable. ...not like your home tank water heater.

 

https://www.amazon.com/Eemax-SPEX35-FlowCo-Kilowatt-Electric/dp/B07MMDH6PJ#immersive-view_1696371592525

 

The sensor - I'm making an educated guess, is the black round jobber with two leads. It's probably controlled via a circuit.

 

An electronics expert could probably figure out how to adjust it.

 

Screenshot_20231003-172006.png

Link to comment
Share on other sites

17 hours ago, XXitanium said:

Your thermostat may be only a set-point. When it gets hot enough, it shuts off. That's what mine does. If the gas water heater eventually sends water hotter than the POU heater thermostat (sensor) requires, it just takes a break.

 


Actually (again AFAIK, I haven’t fiddled with the things for a few years) the unit works by having water pressure energizing a solenoid which in turn energized the heating element. If you want hotter water, you reduce the flow to the unit and vice versa. I have to occasionally reduce the flow to effect a 20 degree rise in temperature. The heating element is probably getting gunked up.

  • Upvote 1
Link to comment
Share on other sites

21 hours ago, SwampNut said:

100% of water heaters have thermostat.  But like the conversation about EV parts and "what is a tachomoter," how it's employed and the results you see may vary.  There is absolute no heating appliance sold in the US that doesn't have an over-temp thermostat.  Now, what other benefits are written into the software controlling it (and yes, pretty much everything has some form of crude software), will vary.  And as you noted, even just an "on" command could still mean you run past the heating ability.  I would expect better quality units would use good software PIDs and a high-watt heater to hold a fixed temp no matter what.  Would be easy really.  PID software is commonly used for everything that needs to have predictive control, from quadcopters to advanced cruise control to...heating...

 

 

My tankless doesn't have a thermostat.  The water temp is based on the size of the fire which is based on water flow, but there's no sensor for it to know what the water temp is.  There's no electronics, it's purely mechanical.  Two knobs let you set the minimum flow cut-in and max fire size, then it regulates from there.

 

It does have an over-temp switch in the flue and another in the water outlet.  Both are switches, no regulation, they shut the gas off if either gets too hot.  They shut the valve off completely so you have to re-light the pilot.

Link to comment
Share on other sites

On 9/7/2023 at 11:02 AM, XXitanium said:

I think that manual is a lawsuit waiting to happen.

It's probably Chinese, they don't care.

 

The wiring diagram on my milling machine's motor is worse than useless.  I had two other people look at it to make sure I wasn't seeing it wrong.  When wired as shown it instantly blows the 30A garage fuse.

  • Upvote 1
Link to comment
Share on other sites

On 10/4/2023 at 8:31 AM, superhawk996 said:

The water temp is based on the size of the fire which is based on water flow

Add in the incoming temp. Montana that can be in the low 40s - Phoenix summer you can't get colder than 65

Link to comment
Share on other sites

11 minutes ago, OMG said:

Add in the incoming temp. Montana that can be in the low 40s - Phoenix summer you can't get colder than 65

Yea.  In the summer I can't get the water cool enough to shower comfortably without the heater shutting off due to insufficient flow to keep it 'triggered' on.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

Terms of Use